The power recently went out in my garage. When I went to the garage and flipped on the light, there was a small spark from within the switch box (where the wires enter the garage) and then no power. Note that my garage was built in 1950, and the wiring is a bit scabby. The garage breaker is a 15A that is in a sub-panel in my basement.

I opened up the wall, and the wiring is brought in and split in two branches: one to the outside receptacle, and one to the lights + a receptacle.

The hot is connected to 3 other wires (via wire nut), one to the light switch, one in parallel to the lighting (or receptacle…I'm not too sure), and one to the out door receptacle.

The Neutral is connected to 2 other wires (via a wire nut), one to the lighting and one to the out door receptacle.

The ground is grounded directly to the light switch body.

I have found that there is correct voltage between the hot and the Neutral only when:
1) There is no load on the out door receptacle
2) The lighting Neutral is not in contact with the garage service neutral

Basically, the voltage is only correct if the entrance Neutral has no load on it from either branch. When there is a load, the voltage goes to zero.

Does anybody know what's going on?

enter image description here

Best Answer

Ok ,you megged it's you know more than most home owners.

This sounds like a broken conductor.

With a light load everything works. Add a few amps and the arc separates the wires. You have megged it so you know it is not going to ground. The only other problem that I have seen like this is from "back stabs" or broken conductors.

With the age of your home I would look for a broken wire in an outlet that daisy chains to the next outlet.

That or a problem in the panel.

After reading everything again your Fluke meter may be the problem with "leakage" or "phantom" voltages. I can say this as a profesional that uses many diferent models of fluke meters & meggers.

Very high impeadance meters will show a normal voltage with no real coper to copper connection.

Some times the voltage is from leakage on solid state electronics. Other times I have found moisture & dust enough to cause phantom voltages. Once a load is on the circuit the voltage is gone.