Electrical – GFCI’s on BLACK/RED dual 15-amp circuits

electricalgfciwiring

I am in the process of updating the wiring for my dock. It was originally wired with a single 15-amp GFCI outlet into which the two motors for the boat lift were plugged into. The problem I’ve had is that I can only operate one motor at a time. If I try to run both motors at the same time the 15-amp circuit breaker back in the sub-panel, located at the beginning of the dock, trips.

I have two 15-amp circuits coming out to the subpanel, from a double-pole (tandem) 15-amp breaker in the house. This is a standard 3-wire with ground format (black, red, white, ground). I’m in the process of putting in a 2nd GFCI outlet, in a larger box along with the original outlet. One outlet will be powered by the black circuit, and the other will be powered by the red circuit. The motors will then plug into the separate outlets. So far so good, I think.

Question(s) are:

  1. How to handle the white (neutral) line. Can this be shared between the 2 GFCIs?

  2. When both motors are running, the current in the white return line will be close to zero, since the current through the 2 motors will be 180 degrees out of phase. Won’t this cause the GFCIs to trip?

Final Results 3/18/2020

Here's what I ended up with:

  • Two GFCI outlets (WR/TR), one on each 120V phase.

  • The load (protected) side of each GFCI feeds one of the lift motors via a switch for controlling lift direction

  • Everything works OK, no GFCI or ckt breaker tripping.

Waiting to get the boat back from winter storage.

enter image description here

Best Answer

To start with, this is a shared neutral aka multi-wire branch circuit. One rule of MWBCs is that neutrals must be pigtailed when the other hot is near; you can't daisy-chain neutral through a device like a receptacle, because that would sever neutral for the other side if you removed it.

Keep in mind on a plain recep, all screws are LINE. There is no LOAD on a plain recep, because it doesn't do anything special like provide GFCI protection, dim, etc.

If you leave the warning tape on the LOAD terminals and don't use it, then you don't have any worries about GFCIs tripping from miswiring. The only time you'd get in trouble is if you did that thing with daisy chaining neutrals, that thing you're not allowed to do anyway, and tapped a recep's LOAD terminal for that purpose - in that case, you are correct, the GFCI would have a problem with that.

However, there's a safer way to wire your dock

Delivering GFCI protection at the socket is better than nothing, but there are all sorts of wire failures before the receps that could leak current into the ground around the lake. And many miswirings could cause the same effect.

Further, outdoors is a terrible place to put a GFCI device; they fail all the time there.

So you are actually better off fitting a 2-pole GFCI circuit breaker back at the service panel... And then you don't need any additional protection dockside. The's no need to put a GFCI on a GFCI. This will protect the entire cabling run, as well as all wiring dockside.