I bought a new construction home in 2005 in Calif. I have a total of 4 GFI or GFCI's. For the past couple years every morning when I get up at least one of the GFCI's is tripped. One of the GFCI's has nothing plugged into it or any of the sockets it controls and it even pops off sometimes. It started with just one doing it and now all 4 are tripping. It's usually very early in the mornings when they trip. Had an Electrician come out and he just took 2 of them out and put back in and another one he replaced and said all is good. But still every morning I wake up to at least one that's tripped. Any idea what's causing this?

Best Answer

If the receptacles are in the kitchen and they serve the countertop they are required to be protected by a GFCI. Whether they are within 6' of the sink doesn't matter since around 1987.

Are they all on the same circuit?

You would not need more than two (normally) to feed the two small appliance branch circuits in a kitchen. Then you feed normal receptacles off the load side of the GFCI.

If they are tripping all by themselves without plugging anything in I would suspect they are miswired. Someone fed one GFCI off the load side of another or fed the receptacle itself by the load wires instead the line wires.

Second, you have a pinched hot wire on the load side of some of them causing enough current to leak to ground to trip them.

The third possibility would be they are really junk and should be replaced but even the cheapest GFCI's have worked for me. And since you already had an electrician replace at least one of them and check the other two I would say this possibility is remote hence I listed it last.

If you have a warranty keep calling for service until they fix the problem.