Do I need to run a ground wire with conduit? I have installed a line of lights using 1/2 EMT and tied into another circuit that is grounded coming off the panel. There are about 7 lights in a back room at my business. In addition, should the last light in the circuit feed back to the panel? The lights are just for supplemental lighting in the work areas.
Electrical – Ground wire with 1/2 EMT Conduit
conduitelectricalgrounding
Related Solutions
Either the junction box has power on it because of some loose hot wire or the ground itself has power on it because of a loose wire somewhere along the circuit.
Most likely though, since the ground doesn't blow the breaker on it's own, the junction box is powered somehow. In one way or another, power is feeding through that box. It could be from the sheathing of the BX or any stripped or loose hot wire touching any of the system. Go back and double check all connections, something isn't right. Be safe.
Wiring methods
EMT and other fixed metal conduit works as a grounding path, so you only need ground wire where the conduit is otherwise. Green, green/yellow or bare is allowed for ground wire. You don't need a ground wire per circuit, only per conduit, but it must be large enough for the largest circuit present. If bare, it must be copper outdoors.
You join a ground wire to EMT by getting a #10-32 screw and fitting it in the pre-threaded hole in the junction box. Do not use a sheet metal screw.
Conduit outdoors in conduit is outdoors. It's pretty much a foregone conclusion that your conduit will fill with water at times no matter how much you try to seal it... that's why you use THWN wire. It's designed to soak.
I have no earthly idea why someone would use solid wire in conduit, perhaps because they were buying (cheaper?) receptacles and switches not listed for stranded wire, or because they were a Romex Kaiser**. It's not worth "fixing", but I wouldn't do any more of it. It's fine for them to mix, just make sure your devices are listed to take stranded wire, and notably backstabs are not, but those are unreliable in any case.
Stranded wire costs about 5% more here. After your first time wrestling 6 solid wires and a GFCI into a 22cu.in. box, you won't mind paying 5% more.
Pulling
You have a tough pull due to the four bends, so gear up for a big one. THWN-2 is already pretty slick and lube won't be worth the unbelievable mess IMO.
The main way to prevent damage is first to thoroughly de-burr, and second prevent kinking, by watching the wires as they enter.
You cannot splice inside the conduit body. Out of the question.*
Pulling one wire at a time isn't better, it's worse. The big hank of wires will mutually help each other as well as provide added strength, whereas pulled individually the existing wires will drag on the new. Don't tape them mid-run, they need to slide a bit to go around corners.
Similar circuits
Beware of NEC 225.30, which generally prohibits running two similar circuits to a building. So having two unswitched 120VAC circuits may be disallowed. However 225.30(D) considers them dissimilar if they are switched, or a different voltage (240V). So the quickest way to clear 225.30 is put one of the circuits on a switch for some reason. Nowhere in the code does it require you to use the switch.
Marking wires
Tape is the key to marking when you don't have 8 colors of wire.
Don't distinguish wires unnecessarily: for instance the two hots going to a 240V heater or 120/240 dryer don't really need to be distinguished from each other.
In your case you need to distinguish two hots from each other, and two neutrals from each other (why? Because you might put a GFCI on one), and potentially a third spare hot.
You can put any tape color on any wire color, but it doesn't always do what you want:
Same-color tape is a little subtle, but is useful for marking. With colored tape it usually doesn't quite match the color or finish of the wire, and you can feel it.
In cable, it's easy to tell which wires are partner to a white, since they emerge from the same cable. This can drive you crazy in conduit with 4 whites coming out of a conduit. In conduit, remarking whites to a hot is disallowed (in most cases) but this cuts both ways: you can use the colored tape to distinguish different wires.
* To be pedantic about it, Code says any box/body is only a conduit body until you splice in it, then, it's a junction box... and must use junction box fill rules. This makes them way too small to splice in, in practical application. Even if the conduit body is wildly oversized for the wire, making the splice strangles the remaining capacity of the conduit, defeating the purpose "room for expansion" to oversize.
Now to be super, duper, duper pedantic, literally NEC says conduit bodies use conduit rules, but they have anything but thru wires, they are still conduit bodies but have to use special fill rules that are identical to the junction-box fill rules. And then, junction boxes use junction box rules, unless they have nothing but thru wires, then they are still junction boxes but use special rules that are identical to the conduit body rules.
** you can tell when conduit work was done by someone used to working in Romex, because they stay as close to Romex practice as possible, e.g. choose only black, white and red for the wires, and occasionally use a white for a switch loop. The old WWI German flag colors. Add green and you have the Pan-Arab colors LOL.
Best Answer
Not if you don't want to. The EMT piping is itself a valid ground path, provided there is a ground path that is continuous back to the panel. All my work is in EMT and I don't own any green wire.
If you need to bond from the EMT to a ground wire, most likely there is a hole tapped for a 10-32 screw on the metal junction box, it may be sitting up on a pucker to give the ground screw some clearance.
UK-style "ring circuits" are illegal in the United States and the wiring of the circuit should not be looped back to the panel.
Sometimes conduit winds up being laid in a ring simply out of coincidence but the wires inside do not go in a loop.