I have a NuTone model QTN130LE1 ventilation fan/light. I have 2 switches on the wall. One is for the light,the other is for the fan.im not sure how to wire it up properly. I don't think I can use the nightlight because I don't have consistent power to the unit,unless a switch is on. I have a black,white,red and a bare ground wire for power. From what I can see,the red wire is coming from the fan switch. The unit has a green,taped red and white,taped white and blue,and a taped together black and white wires. Any help would be much appreciated.
Electrical – Help for wiring a bathroom exhaust fan
electrical
Related Solutions
The three pairs of wires correspond to the three functions. You should be able to find labels or a note in the manual explaining which is which, but for now I'll assume:
- black/white: main light
- red/white: fan
- blue/white: night light
The green wire is a ground wire.
How you wire this up depends on what you have available. A 3-way switch will not help you here; you need multiple switches, and for that to work you may need more wires between your switch box and your fan/light fixture. Most likely, you will have a single cable (with a black, white, and bare ground wire) running to your fan. In that case, you can wire it up as follows:
- bond the bare ground wire with fixture green ground wire
- bond the supply white (neutral) with all fixture whites
- bond the supply black (hot) with the fixture black, red, and blue
That assembly will work, but it's not ideal as your fan, light, and night light will all turn on/off from a single switch.
A better version would be to have two switched wires running up to the fan. You can do this either by adding another 2-conductor cable (such as 14/2WG) running up to the fixture, or you can use a 3-conductor cable (e.g. 14/3WG) where there is a single neutral (white) and two switched hots (black and red). Assuming you have the 3-wire cable, your setup would be:
- bond the bare ground wire with fixture green ground wire
- bond the supply white (neutral) with all fixture whites
- bond the supply black (hot 1) with the fixture black and blue (lights)
- bond the supply red (hot 2) with the fixture red (fan)
This allows you to control the fan and light separately with your two switches, but again has the shortcoming that the nightlight is only powered when the light switch is on. Which probably defeats the purpose!
And that leaves the final, best option: two switched hots as above, plus an unswitched hot power supply wire (let's call it black-unswitched). In this setup, you'll
- bond the bare ground wire with fixture green ground wire
- bond the supply white (neutral) with all fixture whites
- bond the black-unswitched supply with the blue (nightlight)
- bond the supply black (hot 1) with the fixture black (main light)
- bond the supply red (hot 2) with the fixture red (fan)
This setup is ideal because you have switches to control your fan and light separately, and you have constant power to supply the night light. That means your fixture can use the unswitched power to run the nightlight constantly, and when you come in and turn on the main light, the nightlight either turns off or just becomes irrelevant.
As you can see, you have a few reasonable options for how to wire this fixture. Another variation is that you might have unswitched power in the fixture area, and only one cable running to your switch box. If that is the case, you'll be using the cable to the switch to both send power to the switch and receive power back when the switch is on. If you have that sort of set up, you could provide constant power to the nightlight even if you have a single switch controlling the fan and light together. You'll need to make a couple more junctions in/near the fixture in this case, involving the switch.
Note: a 3-way switch will not be helpful. A 3-way switch has three wires (call them A,B,C) and allows you to switch between connecting A+B or A+C. Two 3-way switches can be used together to allow switching a light from two locations. But as long as you have a switch with only two positions, you can only choose between on and off, not off, on-fan, on-light, and on-fan+light. For that you need two switches, or some sort of switch designed to control two separate fixtures.
Final cautionary note: To do this right, you will need some basic electrical knowledge, including how to properly connect wires with wire nuts and how to work on a fixture safely. If you aren't familiar with this sort of electrical work, you should get someone who is (experienced DIYer or pro) to work with you. Improper electrical work has a massive risk of hurting you, either while you're trying to install it or later on when a failure can put you at risk of fire. Good luck and be safe!
You are not wired the same way as the picture in your instructions. I think the power comes in to the ceiling box, and the switch is a separate cable.
To verify this, disconnect all of the wiring in the ceiling box and at the switch. Turn the breaker on and carefully check for voltage between the black and white wires. When you find the black and white pair (or just the black wire if you are using a voltage tester) that has power, then you can turn the breaker off.
If this test confirms voltage on just one black wire, then connect as follows:
- In the ceiling box:
- Connect the black powered wire to the other black wire in the ceiling box.
- Identify the white wire that is paired with the black powered wire. It will be in the same cable sheath. Connect that white wire to the white wire on the fan.
- Connect the remaining white wire (which would be coming from the switch) to the black wire on the fan/controller. Wrap a piece of electrical tape around the white wire about a half inch back from the wirenut. This will signify that the white wire is carrying live current and is not a neutral.
- In the switch box:
- Connect the black wire to the switch wire with the yellow sticker.
- Connect the white wire to the switch wire with the blue sticker. Also mark this white wire with electrical tape.
Related Topic
- Electrical – Help wiring Bathroom fan
- Electrical – Wiring a ceiling fan and light switch with two three-cable wires
- Electrical – Rewire wall switch to an on/off switch, for a ceiling fan that has nightlight, fan & lights
- Electrical – Wiring Ceiling Fan Remote, Two Dimmers
- Electrical – Bathroom exhaust fan wiring
- Electrical – Two wall switches and remote ceiling fan/light questions
Best Answer
Your green wire from the fan gets connected to the bare copper wire from your ceiling box. Then connect the white wire taped with the blue to the white wire taped to the black to the white wire from your ceiling box. Then connect the red wire from your switch to the black wire from your fan and connect the blue wire from your fan light to the black wire coming from your other switch. The remaining red and white wires from your fan fixture are for the night light which you would need another switch to operate it