Electrical – Home Inspector reported two 20 amp breakers not allowed in panel per manufacturer

electrical-panel

Home Inspector reported two 20 amp breakers are not allowed in electrical panel per manufacturer (Eaton MB1212L200BTSA). He said there must be single bar over both breaker to connect together? Is there a clip that I can attach to make both breakers trip at same time?
Here is pic from inspection report.
Image of breakers

See the red arrows, he said these two 20 amps must be tandem and a clip connecting both switches?

One 20 amp powers a GFI receptacle the other 20 amp powers a platform lift. I need to keep power separate for 110 volt. I do not want 220 volt. Do I need a double-pole 20 amp that has handle ties?

The electrical panel was installed in 2012. Is it correct to install a BR220 and use it for two 110 volt circuits?
Going out to purchase BR220 breaker, anything special to know about attaching wires from the two single points to double poles?

Best Answer

One throw too far

Your meter-main was designed to use a set of smaller sub-main disconnects instead of a single main disconnecting means, in accordance with NEC 230.71:

230.71 Maximum Number of Disconnects.

(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No.1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or in switchgear. There shall be not more than six sets of disconnects per service grouped in any one location.

For the purpose of this section, disconnecting means installed as part of listed equipment and used solely for the following shall not be considered a service disconnecting means:

(1) Power monitoring equipment

(2) Surge-protective device(s)

(3) Control circuit of the ground-fault protection system

(4) Power-operable service disconnecting means

(B) Single-Pole Units. Two or three single-pole switches or breakers, capable of individual operation, shall be permitted on multiwire circuits, one pole for each ungrounded conductor, as one multipole disconnect, provided they are equipped with identified handle ties or a master handle to disconnect all conductors of the service with no more than six operations of the hand.

However, the pair of single pole breakers in the lower-right that the inspector complained about means that you need 7 breaker throws to turn all the power off, which is one too many.

Evict the aliens!

Furthermore, the culprit breakers are a violation by themselves as they are GE THQLs, which are not listed to go in an Eaton BR panel. At this point, you might as well get a BR220 from the nearest supplier and have it slapped in in place of the culprits, killing two violations with one fix.

And yes, a two pole breaker can feed two completely separate 110V circuits

There is nothing in the NEC that prohibits a two pole breaker from feeding two independent branch circuits from the opposite legs it provides.