Best Answer

You have two options:

  1. use tandem breakers
  2. Install a sub panel

There are caveats with both routes. When using tandem breakers on a 120 volt system (i.e. with a neutral present), you want to avoid something that is called a multifeed. This is, two circuits on the same phase sharing the same neutral. When using tandem breakers, its very easy to inadvertently do this.

If you are in the US, you will see two feeders from the meter, one of them probably has some red tape on it, the other is black. These are your phases. Normally, every other breaker is on a different phase, but tandem breakers put both circuits on the same. Take care that both circuits attached to a tandem have their own neutral (white wire).

While you might be able to install a tandem breaker yourself (I highly recommend calling a qualified professional), you will surely want an electrician to install a sub panel. They aren't much different from a regular panel except:

  • Ground and neutral conductors are isolated, not bonded on sub panels
  • You want to watch your loads
  • You'll want to be careful about where you place the breaker that feeds a sub panel, so that you don't develop a hot spot on the main panel bus. For instance, you don't want a 100 amp sub panel breaker right in the middle of a water heater and an air conditioner.

In either case, I really recommend calling an electrician.