Electrical – How to convert an existing electrical panel to a subpanel

electrical-panelsubpanel

I'm going to upgrade my existing electrical service from 100 amps to 200 amps. Along with the service upgrade, I'll be moving the location of the service drop (part of a larger home remodel). I want to keep the existing 100A panel (which mostly serves old K&T and original NM spec wiring) as a subpanel. I'll add new circuits to the new 200A panel, and over time decommission the circuits fed by the 100A panel.

I'll add a 100A breaker in the new panel. But my existing panel has a non-removable main breaker (rated at 100A). Is this allowed?

Are there other considerations?

Best Answer

Main breaker

There's no problem with having a main breaker in a subpanel. It's required if your panel is in a separate building and has more than six breakers, but there's nothing prohibiting it in any other case.

Wire size

You need to ensure the wire between the panels is sufficient size. See What wire gauge do I need for a 100 Amp subpanel at the end of a 60' wire run?

Neutral-ground bond

You need to ensure the only bond between ground and neutral is in the main panel. The subpanel must have separate ground and neutral bus bars. Since your panel is used a main panel now, it will currently have a bond between ground and neutral, so that'll have to be removed.

  • It's usually a metal bar or connector that screws between the two bus bars, or between the cabinet and neutral bar.
  • If you currently have neutrals and grounds mixed on both bus bars, you'll have to separate them out
  • If you have only a single bus bar (with grounds and neutrals mixed) you'll have to add a neutral bar (which is not bonded to the cabinet). Check with manufacturer first to see if they have a documented way of doing this. If not, I'd suggest you check with your AHJ (inspector) first to be sure whatever you do will be acceptable.