I am designing the circuit(s) for my basement apartment (cca. 800 sq ft) baseboard heating solution. I am planning to buy Berko HBB Series heaters and distribute them as shown in the below table. All have a voltage of 240/208.
Location Model Length(in.) Watts Amps
-----------------------------------------------------------
Living Room HBB1504 70 1500/1125 6.3/5.8
Bath HBB504 28 500/375 2.1/1.8
Bedroom HBB1254 58 1250/938 5.2/4.5
Hallway HBB754 34 750/563 3.1/2.7
My questions are:
- Should I split them into two circuits (living room and bathroom in one, bedroom and hallway in the other) or is it OK to keep them all on one circuit?
- Is the voltage a factor in determining the wire gauge? I know that the amperage is. E.g. if I split them in two circuits so that each circuit bears less than 10A each, can I go with AWG 14/3 even though the voltage is double than usual? Or simply put, which AWG should I use for either scenario from question 1.?
I have an extensive experience as a DIY electrician, I have pretty much rewired most of my house and have set up one 240/120 circuit for my dryer (used AWG 10/3). But this is considerably lower amperage so I am not sure what AWG to use.
Best Answer
Sizing conductors and breakers
Almost all wire you can buy will be rated at 600 volts, so you won't have to worry about voltage when sizing wires. What really matters is current. Your wires will be sized to carry enough current for the load, and your breaker will be sized based on the wire used.
When installing electrical devices, it's always a good idea to check the manufacturers installation instructions (PDF). In this case, it has this to say...
As the table shows, you can connect up to 24 amperes worth of heaters to a single circuit. However, if you do this, you'll have to use 10 AWG conductors and a 30 amp breaker. If you only want to use 14 AWg, you can only put 12 amperes worth of heaters on a circuit.
Number of conductors
Since these are 240 volt heaters, you'll only need two conductors (plus a grounding conductor). If you're going to use nonmetallic sheathed cable (Type NM), you'll need AWG/2 with ground, not AWG/3 with ground cable.