I need to bring a 1/0-1/0-1/0-2 AL SE cable from a 2×4 wall into the back of the main service panel (it is a new subpanel feeder).

The main service panel is surface-mounted on the outsde, on the siding. The wall is 2×4, wood T111 siding, drywall inside (garage) and can be exposed/accessed easly from inside.

It seems the 3.5" of space in the wall is rather tight for the 1/0 AL NM cable to bend.

  1. is it possible (to code) for the cable thickness to fulfill minimum band radius (MBR)?

  2. what fittings to use? (do they need to be liquid tight as the connection to the panel is kinda on the outside (well…panel-on-siding wall but there is no waterproofing there)?

  3. any ideas and advices to solve this problem?

I was thinking about using a conduit right angle fitting to ease the bend (strip the outside sheathing from the SER to ease MBR, after it enters the fitting) but not sure if code/inspector/sanity allows it and how to secure the cable to the fitting?

The new cable is labeled: ALUMAFLEX AA8178 TYPE SE STYLE SER TYPE XHHW-2 CDRS 600V

BTW, There is already an existing, in-service sub panel feeder which enters from the rear via a regular NM clamp connector. The old cable is "thinner" so the bend was easier (though still 100A breaker). This must have been inspected as it was installed when new 200A service was installed so a non liquid-tight was ok?

enter image description here

Best Answer

On a seemingly unrelated topic, I like to see houses have LOTS of spare breaker panel spaces. Spaces are cheap, and in the future stuff always comes up, and nobody has ever said "Oh no, I have plenty of breaker spaces available, whatever will I do?"

Hold that thought.

Now, given the thickness of the cable, I do not see way to make that bend. What I advise doing is installing a LARGE junction box on the inside of the garage wall. Now your SE-R cable can enter that box vertically, transition into individual wires, and go through a conduit nipple from this inside box to the outside box. At that point we're only concerned with radius of individual wires, and that's no problem.

Now let's price that. Splices of large wires require very long, tall boxes. We also need splice connectors for 1/0 wire (four of them)... Hold on a minute. What's a LARGE box that comes with big lug connectors, that's cheap?

Why a subpanel, of course!

So if extra breaker spaces wouldn't be useless, the best answer may be to fit a large subpanel on the interior of the garage. "Large" because you want full width, and enough height to handle the large wire bends. A 14" wide psubpane gives you

And that's exactly what I'd do. Select a 200A-bussed, main-lug but convertible subpanel of 20+ actual spaces (not circuits).

I'd arrange the new panel back-to-back with the existing panel, using a "nipple" to connect them that is as large as the knockouts allow.

Downhill from there.

If the SE-R cable's internal conductors have their own markings (as XHHW conductors) then you can enter the new subpanel with a grommet/cable clamp, then pass right through the new sub and into the original panel - at that point you're just using the sub as a giant junction box.