I currently have in my shop, a 20 amp outlet directly below my panel which is approximately halfway along one of the walls. Instead of having the GFCI outlet at the end, I would like to replace the existing outlet with a 20 amp GFCI outlet and add regular outlets to the left and to the right of it along that wall. Can I pigtail the black and white wires? Will the outlets be protected?
Electrical – How to install a GFCI receptacle to provide protection to other devices
electricalgfciwiring
Related Topic
- Electrical – How to wire a GFCI receptacle using two black wires and two white wires
- Electrical – Why is the GFCI receptacle tripping when I add another receptacle to the circuit
- Electrical – How to wire GFCI outlet
- Electrical – have a 15 amp outlet on a 20 amp circuit with a 20 amp GFCI
- Electrical – GFCI protection for multiwire branch circuit in shipping container workshop
- Electrical – convert a fused dryer outlet to two 20 amp circuits
- Wiring – How to intall GFCI breaker if wire for outlets is 12/3 using two breakers
- Run hot wires for both GFCI-protected and non-protected branches in one conduit
Best Answer
Yes, look carefully at a GFI (or equivalently GFCI) outlet:
You can see the terminals at the top are labeled Line which means, upstream power. The pair of terminals at the bottom are labeled Load, which means this is where to connect outlets downstream which are protected by this GFI.
Be careful not to bridge the line terminals to the load terminals! A pigtail should only connect to the load terminals.