I have a GFCI in garage that protects one receptacle in the garage and one in the yard.
The GFCI receptacle itself feeds the sprinkler timer. The other receptacle in the garage is hardly used. The receptacle in the yard is used for a small water feature pump.

Occasionally, the pump trips the GFCI. I am looking for a safe solution. First I thought,
maybe I could change the yard receptacle with a GFCI (two GFCI in one line), but I read that is not a good idea. Any safe solution?

Best Answer

You can use multiple GFCI devices on a single circuit, you just cannot connect them inline with each other. If your current wiring looks like this, where the yard receptacle is connected to the load side of the GFCI receptacle in the garage.

GFCI protecting downstream device

You can change the way the second receptacle is supplied, by connecting it in parallel with the existing GFCI receptacle. Then you can swap the receptacle in the yard, with a GFCI receptacle.

GFCI not protecting downstream device

In this configuration, the GFCI in the garage will only trip if a ground-fault is detected in any device plugged in to it. While the GFCI in the yard will trip if any device plugged in to it, has a ground-fault.

If the GFCI protecting the circuit is a combination GFCI/circuit breaker, you'll have to swap it out for a regular circuit breaker. Then you'll have to protect individual outlets appropriately, using other GFCI devices.