Electrical – How to qualify for the 75C table in the ampacity chart

electricalnecwiring

Suppose we direct-buried some 8 AWG cable. It's now under a parking lot, and retrenching it is out of the question. Now, needs have changed and we need to get 50A out of the circuit, which is possible with 8 AWG in the 75C column. The wire is good for it.

What else is needed to qualify to use the 75C column?

Does anything change if this is wired in the interior of a house?

Best Answer

UF can't beat the heat

Unfortunately for you, UF cable is like NM in that it can't be run at any higher temperatures than 60°C:

340.80 Ampacity. The ampacity of Type UF cable shall be that of 60°C (140°F) conductors in accordance with 310.15.

Now, if this were a tri-rated (USE-2/RHH/RHW-2) multiplex cable, or a direct burial MC cable, it would be something of a different story, but that's beyond the scope of this answer.