Electrical – How to splice grounds in a metal box with a 30amp and 20amp circuit

electricalgroundingwiring

I have a 30amp dryer circuit (4×10 gauge – 2hot, 1neutral, 1gnd) and a 20amp circuit (3×12 – hot, neutral, ground) coming into the same metal box. The 20 amp circuit continues on to another box where the 20amp outlet is and the 30amp outlet is in this box.

Do I need to splice all the grounds together in this box (and to the box)? Or, can I directly connect the 4×10 to dryer outlet (without any splices with the 20amp circuit), then splice the 12gauge ground together and to the box?

If I do need to splice them all together, do I need to use 10AWG to the metal box?

EDIT: Basically I'm wondering if doing something like this is acceptable, or if I need to also to connect the incoming line to the 30amp dryer outlet to the ground bundle.
enter image description here

Best Answer

Splice the ground wires together and to a box ground pigtail

You'll need to splice the ground wires coming into the box to each other and to 10AWG pigtails to both the receptacle ground terminal and the box grounding screw, as per NEC 250.148. That way, there's a direct path for ground current from the MC's ground conductor to the ground wire in the FMC, instead of sending ground current from the MC cable through the box and the yoke of the NEMA 14-30R in order to get to the ground wire in the FMC (or equivalently, through the box and then the 5' of FMC to get to the next box).