Electrical – How to stop this GFCI receptacle from tripping

electricalgfci

In my garage I have two wall receptacles on opposite sides of the garage. On one side the receptacle is a GFCI receptacle and the other side is a normal one. In the normal receptacle I have a small deep freeze, and a refrigerator plugged in. A couple of times a day I go out and neither the refrigerator nor the freezer are working, and the GFCI receptacle on the other wall is tripped.

Any suggestions on what I can do to fix this?

Best Answer

The below steps describe how to disable a safety feature by removing GFCI protection from your circuit. Check with local codes and verify that the problem isn't simply a bad GFCI or malfunctioning appliance before considering following these steps.

It sounds like your normal outlet is wired to the GFCI, making it a protected outlet.

Turn the power off, and remove the GFCI. You should see Black and White wires connected to the "LINE" Terminals, and another pair Connected to the "LOAD" Terminals. Devices with motors can trip GFCI outlets due to inductive loads at start up or shutdown.

Get yourself some spare wire. If you don't have any, buy a foot of 14/2 household wire from the local Orange or Blue Big Box Store. Also pick up some wire nuts rated for 3 14 ga wires.

You'll need to cut 4-6 inch white and black "jumper" wires and strip the ends.

Disconnect all wires from the GFCI, and screw in the LOAD screws all the way. I like to tape them off with electrical tape.

Attach one end to the LINE Terminals, matching white to white and black to black. (Brass screw is black, Metal screw is white. Green screw is ground (green or bare).

Now wire the three white wires together with a wire nut. Similarly, wire the blacks. These are called Pigtails.

enter image description here

Wire the two remaining ground wires to the ground (green) screw on the GFCI.

Stuff the wires in and re-mount the outlet.

You've just unprotected the fridge and freezer. However, I'd put a label on the unprotected box "NOT GFCI" so that a future owner doesn't make any assumptions.

EDIT: There may be a code requirement to have all garage circuits GFCI protected. Check with your local authority before doing this.

NEC 2008

210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.

(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use.