Electrical – How to two different breakers both turn off the same circuit

circuit breakerelectrical

I have a 40 yr old home with circuit breakers. While looking for the breaker to turn off a circuit (I was replacing a light switch), I found that two breakers, on the same side of the bus, but separated by a few other breakers, both disconnect the circuit. To be clear, I am telling you that I can turn off either one of these to kill the hot wire in the switch box. The only thing I can think of here is that somehow one of the breakers is feeding the other. I've never seen a circuit behave like this.

This is similar to the other thread on this site about "Two breakers switches control the same thing" except in my case, I have the opposite result: either of the two breakers will kill the circuit.

Is there any reason this may have been done on purpose? Is this allowed by code?

Best Answer

That could be a split bus panel, meaning that there are two sets of power distribution buses. It used to be allowed by something called the "6 handle rule" (which allowed up to six of them in a service panel) back when circuit breakers cost a small fortune.

They were wired like this:enter image description here

And might look like this: enter image description here
Note the gap in the breaker buses at center where there are no breakers, but you can see heavy black wires connecting to the right end of the secondary buses.

The cables from the meter connect at right (which would conventionally be the top of the panel) and feeds the six double breakers. Five of them feed directly to heavy loads: range, water heater, dryer, baseboard heaters, etc. The top-left double ganged breaker feeds the second bus in the left half of the photo.

In this configuration, any circuit fed from the lower bus would be shut off if either its own breaker were switched off, or the feed breaker—which also shuts off almost everything in the building.