I have a sub panel in my detached garage. I wanted to change the sub panel. I found that it is a 3 wire feed, neutral, and 2 hot, no ground. The panel is connected to the metal conduit coming in from the floor, but the conduit ends when it reaches the basement in the house about 60’ away. It does not connect to the main panel. It doesn’t seem to be properly grounded.

How can I change the panel properly with out pulling a new 4 wire to the garage from the main?

Best Answer

Assuming your conduit is continuous from your basement to your subpanel, your best option is to use it as your ground path. Metal conduit is an excellent ground conductor, and can easily handle hundreds of amps, even when a little rusty.

Buy a conduit ground clamp, such as this one:

Conduit Ground Clamp (Image courtesy of Home Depot)

Then, run an appropriately sized green or bare copper wire from the end of the conduit in your basement to your service panel, or any point along your grounding electrode system. This will complete the ground path from your subpanel back to your main panel.

Now, to complete the conversion, shut off the breaker feeding your subpanel, and remove the neutral-ground bond that's likely in there. This may require moving neutral and ground wires onto separate buses if they're currently mixed.

If you're not sure the conduit is continuous (i.e. it might transition to plasitc somewhere underground), you can now test that with a multimeter and an extension cord: Plug it into any regular outlet in the house, walk to the subpanel in the garage, and test for continuity between the round ground pin of that extension cord and the metal conduit going into your subpanel. If it has continuity, you're good to go. If not, now pull another ground wire through the conduit and connect it at the subpanel and main panel/grounding electrode system (but still leave the conduit clamp connected as well -- it's good to bond conduit to ground even if it isn't serving as a ground path).