Electrical – How to use a 100 amp sub panel for a 50 amp input

circuit breakerelectricalelectrical-panelsubpanel

I'm building a shed I want to add power to. To get power I'm planning to use the power that is going to my hot tub (50 amp).

The hot tub has a 50 amp breaker from the main to a 50 amp breaker box that is mounted on the side of my house. I plan to disconnect the hot tub and run the wire to my shed from this breaker box.

I can't find a 50 amp sub panel, but I can find 100 amp boxes online that are fairly cheap. I'm curious how I can wire this box to use the 50 amps that will be coming in?

Best Answer

Just wire it up. There is no problem using a sub panel that can take more current than you will ever feed it.

Points to note:

  • The cable to your hot tub will be rated for 50A (not 100A); therefore you must not upgrade the breaker in your main panel to 100A.

  • It would be sensible to add a note near the main panel that the cable is only rated for 50A, so not to change the breaker (so you, or a future purchaser, remembers in a year's time).

  • If you connect four 20A 240V devices to the sub-panel in your shed (and run them all at once) the sub-panel will be entirely happy with this, but the 50A breaker in the main panel won't be and it will throw - so don't do that then.

PS. This is not directly related to your question, but still. 50A is a substantial current. Do remember to torque the connection to the panel correctly.