I have a single gang box in a bathroom with a GFCI outlet. I'd like to replace it with a 2-gang box containing a GFCI outlet and a light switch for the vanity light. The outlet will have both receptacles live (not switched).

The vanity light currently is not switched; it is controlled by a pull-chain on the light itself. We're going to replace it with a non-pull-chain type of light and we want a switch where the kids can reach. It'll be nice not to have to explain to our guests how to use our bathroom, too.

I did some poking around and it looks like the vanity light is fed from a different branch from the receptacle.

One plan is to pigtail the switch and gfci outlet onto the supply line, and then take the output of the switch out of the box up to the vanity light.

Another way to do it would be to run a switch loop from the lighting fixture down into the 2-gang. The gfci receptacle would be wired the same as it is now, and the switch would be on the switch loop.

Is one of these the correct way to do it? If not, how should I wire this?

Best Answer

Since your light is on a different circuit than the outlet, you'll need to run a switch loop from the light to the 2-gang box using 14/3 (yes 3) cable, with black as the hot, red as the switched hot, white as a spare neutral, and the bare or green wire as well, the ground (aka EGC) :)

In the light box, you'll take the black that currently goes to the fixture hot and connect it to the black of the switch loop instead; the fixture hot then gets wired to the red wire of the switch loop. The switch loop white and green wires get wired into the existing white and green wires coming into the box.

After transposing the existing GFCI from the old 1 gang box into the new 2 gang box, you'll want to leave it alone from here on out. To wire up the switch, you connect the brass screws to the black and red wires, the green screw to the EGC, and simply wirenut off (i.e. put a wirenut on the exposed end of) the neutral on the switch loop -- it's there for future use by say a motion sensor or lit switch as per 404.2(C) (neutrals are called 'grounded conductors' in the NEC, btw, if you're a Code newbie and scratching your head at this :):

C) Switches Controlling Lighting Loads. The grounded circuit conductor for the controlled lighting circuit shall be provided at the location where switches control lighting loads that are supplied by a grounded general- purpose branch circuit for other than the following:

(4) Where a switch does not serve a habitable room or bathroom