I had a new 100 amp panel installed in my house 10 years ago. There is one plug in the kitchen wired (14/2) to a 120V, tandem 2 x 15 amp breaker (using only one pole). What type of wiring do I use to wire more plugs and use this breaker properly? Most topics are concerning tandem 240V breakers using 12/3 wire.
Thank you!
Electrical – How to wire a tandem 120 volt, 2 X 15 amp single pole breaker
circuit breakerelectricalelectrical-panelwiring
Related Topic
- Electrical – 240v double pole breaker for two 120v circuits
- Add a 240v outlet inline with a sub-panel supply circuit
- Electrical – Power Outlet -3 Wire Conductor on Tandem Breaker Wiring
- Electrical – Can a single pole (normal/regular) circuit breaker be used in spots designated for tandem
- Replace two Siemens QP type, handle tied, single pole 15 amp breakers with a tandem QT type in the same configuration
- Electrical – Two pole breaker feeding three pole receptacle
- Electrical – 2-pole 30 amp breaker into two individual 120 receptacles
Best Answer
With 14 2 with ground you are limited to a 15 amp breakers as 3phase has stated in earlier post this has been code for many years in the U.S. that's why most outlets in kitchens deal with 12 AWG. If you have 14 awg 15 amp breakers are correct and by putting in a double stuff or tandem you can run a new line to add more outlets or split the existing run to have multiple breakers with the existing runs so 2 appliances or devices won't trip a 15 amp when the next outlet over if fed by the second breaker. Never combine the 2 tandem breakers on the same circuit as this would be a code violation and risk a fire hazard.