Electrical – How to wire multiple lights and a split receptacle to 3-way switches

electricalreceptacleswitch

I have two lights and a split receptacle wired like so:

enter image description here

Now I want to wire a second switch into the room, but I'm having trouble working the split receptacle into the mix. I feel as though 3 conductor cable isn't going to cut it. Am I going to have to run more than one cable? Or can this be accomplished using only one cable run between everything?

The switches are going to be at opposite ends of the room from everything.

Best Answer

If the switches you are using are typical switches and not the new techno type gizmos which require neutrals, then all you need to do is replace that switch with a three way switch and add a second three way where you want the second switch to be. Pull a piece of Romex (3 conductor cable with ground) between the two switches.

Use the red and white in that cable as travelers between the (2)- 3 way switches and the black as your switchleg. That black wire in that cable will terminate underneath the black screw at your new switch location but tie into your wire feeding the lights/receptacle ('red wire in your drawing') at your switchbox that you already have in place.

The hot feed (in your drawing above) will terminate underneath the black screw of the three way switch installed at that box.

Remember, put a piece of red or black tape on the white wire in the cable so that others servicing the box down the road will know that white wire is not a neutral wire.