I have a 30 amp breaker in my main panel, with 12/3 wire ran about 100 ft. To my sub panel in my shed. I'm wondering if I can put a 20 amp breaker for my outlets and a 15 amp breaker for my light in my shed?

I'm running a air compressor about 150 psi for my airbrush and a small heater and my light in my shed at the same time. It's currently on a 15amp breaker in my sub panel.

Don't know much about electrical circuits.

Best Answer

Short answer: yes for the branch circuits, no for the feeder.

The capacity of the sub panel is a total of 30 amps of load NOT the sum of the breakers. As long as the total of all of your equipment doesn't exceed that then you are good.

Edit: Tester is right and I missed that you had 12/3 running to the shed. #12 wire cannot be protected at 30 amps. The maximum for #12 is 20 amps. If you want a 30 amp circuit to the shed it needs #10 wire.