Electrical – Is a sub panel necessary to wire this 10.5kw 43.75amp sauna heater

circuit breakerelectricalelectrical-panelsubpanelwiring

We're planning on installing this Harvia Cilindro 10.5kW Electric Sauna Heater (Model HPC11-U1H) when it gets here.

The manual wants us to put a 50amp breaker in the main panel, and then run that to a sub panel with 2 40amp breakers, before finally connecting them to the power unit box for the heater/controls.

My question is, could I skip that 50amp breaker part and just install the 2 40amp breakers directly onto my main panel? My main panel is 200amps and has plenty of room for more breakers, and both the main panel and the sauna are in the garage so there's no benefit to me installing a sub panel there as well (unless this is a dumb idea and I'll burn my house down unless I do it).

Pictures for reference. Thanks!

Manual

Breaker and Wires

Best Answer

Normally you'd need the sub panel if for no other reason than to have a means to disconnect the sauna for maintenance. Since the sauna is in the same room you can go directly to it from the main panel as long as you have clear line of sight from the panel to the sauna. Your instructions show a sub panel and you shouldn't deviate from them but they also give wire sizes for going from main breaker to power unit (4#8,N & G) so I guess it's OK.

I think going to the sub panel would be cheaper.