Updating wiring for a laundry area, I'm wondering if a GFCI receptacle should be used for the washer.

The washer manual asks for a 15A individual branch circuit. Code says if the receptacle is within 6' of the edge of a sink, it needs to be GFCI. In my case, the receptacle will be located >6' from the nearest sink edge (~10') and 15-25 feet from a water heater and natural gas furnace. (I note the water heater and furnace in the room, just in case that has any affect on the decision.)

So, a GFCI is not required, but should I opt for one anyway since a new receptacle is being installed? Given the circuit will service only a single 15A receptacle, does it need a GFCI or is being grounded with properly rated breaker & wire enough?

Best Answer

NEC article 210.8(A) lists areas requiring GFCI protection and not only are garages listed, but the last item on the list is "laundry areas", with no exceptions listed (nationally, your local codes may vary). So yes, you must use a GFCI either way. The 6' distance exception only pertains to sinks and bath tubs, not laundry areas, because it must be used in the laundry area even if the sink is more than 6' away.