I would like to know if it's allowed to run 10/3 Romex in 3/4 inch PVC pipe for 15 ft. outside under the floor of an open porch to be wired to a 30A power outlet for a portable 6500 watt generator.
Electrical – Is it allowed to run NM wire in PVC pipe under an outdoor porch
electricaloutdoorwiring
Related Topic
- Wiring – Conduit for cable under a porch
- Electrical – Running NM-B in PVC SCH 40 Conduit from Outdoor Breaker Panel
- Electrical – White PVC pipe for electrical wiring
- Electrical – Run 6 AWG NM-B cable through 1 1/2 PVC pipe indoors
- Electrical – Are multiple wire runs in conduit allowed
- Electrical – Wiring up a shop with underground conduit
- Electrical – Can a portable generator power multiple circuits in a house
Best Answer
No. Nonmetallic sheathed cable is not allowed in wet locations. NEC considers outdoor conduit a wet location.
You'll have to use THWN conductors, or other conductors/cables rated for wet locations.
If you use THWN conductors, you'll be able to fit 7 conductors through 3/4" Schedule 80 PVC (Table C.9), or 9 conductors through 3/4" Schedule 40 PVC (Table C.10).