So to continue my line of electrical questioning (and perhaps narrow down my flickering light problem), I took a look through the two panels in this house. There is a 200amp main service in the basement, which then feeds up to a 100amp sub-panel for the main floor. This 100amp sub feeds a kitchen (fridge, microwave, dishwasher, gas range), a bathroom, 3 bedrooms, and a living room. The 200amp main feeds the 100amp sub, 2 bedrooms, a living room, a washer/dryer (gas dryer), a utility room (well pump, pressure tank, gas water heater, gas furnace), and an A/C.
My first concern is that the main service panel has the bare ground and neutral wires mixed on the two bus bars. Reading around, some say this is OK, other's say it is bad. Any thoughts? The sub-panel is wired with grounds and neutrals on separate bars.
My second concern- is a 100amp sub sufficient for the main floor?
Best Answer
This means that the grounded (neutral) from the service must be connected to ground, and that the connection can be made by bonding the neutral bus bar to the grounding electrode.
This means that the grounded (neutral) conductors should only be grounded at the main service disconnnect.
If the main service panel happens to be the same place that the grounded (neutral) conductor is bonded to the grounding electrode, then there is no problem mixing grounds and neutrals on the same bus bar (as long as there is an appropriate number of conductors terminated under each lug). If the two bus bars are not connected; as would be the case anywhere other than the main disconnect (exceptions exist), then you cannot mix them.
Notice how the grounded, and grounding bus bars are connected in the main service panel. This means that; electrically speaking, they can be considered a single bus bar. Which means that both grounded (neutral), and equipment grounding conductors can be terminated on either bus bar.
In the subpanel, the bus bars are kept separate. So grounded (neutral), and equipment grounding conductors cannot be mixed.