I have just installed an outdoor security light with a junction box I bought (weatherproof). I wired the old red source wire to the new brown, old black source wire to the new blue in the terminal block, but noticed the third ground wire was just exposed copper. I wired that to the new yellow and green, but wondered why is it exposed, and will it function OK? I put some electrical tape round it as a little bit of it was still exposed outside the inlet to the junction box. Previously all 3 wires were completely exposed in the terminal block from the previous occupant, which was a little worrying!
Electrical – Is it okay that the earth wire is exposed when installing an outdoor security light
electricallightingoutdoorSecurity
Related Solutions
Sometimes when ceiling boxes are roughed in, they use x/3 with ground cable so that they can supply 1 switched hot, 1 neural, 1 hot/switched hot, and 1 ground to the ceiling box.
This allows a ceiling fan to be installed in such a way that the fan can be controlled either by a separate switch, or using only the attached pull chain. In this situation the red wire in the cable is usually disconnected and capped at both ends, and is only intended to be connected as needed.
You may be able to verify this by opening the switch box, and verifying the wiring at the switch. If this is the case and the extra hot wire is not needed, it should be disconnected and capped at both ends. Once that's complete, you can move on to determining if you have a proper grounding conductor.
Grounding Conductor
If the building was renovated/built in 2008, it's not likely the circuit does not include an ground conductor. However, there are multiple ways to satisfy the grounding conductor requirement according to NEC 2008 250.118.
- A copper, aluminium, or copper-clad aluminum conductor.
- Rigid metal conduit.
- Intermediate metal conduit.
- Electrical metallic tubing.
- Listed flexible metal conduit meeting specific conditions.
- Listed liquidtight flexible metal conduit meeting specific conditions.
- Flexible metallic tubing meeting specific conditioins.
- Armor of Type AC cable as provided in 320.108.
- The copper sheath of mineral-insulated, metal-sheathed cable.
- Type MC cable where listed and identified for grounding in accordance with specific criteria.
- Cable trays as permitted in 392.3 and 392.7.
- Cablebus framework as permitted in 370.3.
- Other listed electrically continuous metal raceways and listed auxiliary gutters.
- Surface metal raceways listed for grounding.
Checking for a Grounding Conductor
The most accurate way to verify whether or not there a proper ground connected, would be to check for continuity between the junction box and the grounding electrode system. In most situations this is not an option, so another test must be performed.
Checking Continuity to the Grounding Electrode System
To run this test you'll either have to be within reach of; or be able to run a lead to, the grounding bus in the main service panel.
- Set your multimeter to the continuity setting or the lowest resistance setting.
- Place one lead on the grounding bus bar in the load center.
- Place the other lead on the junction box under test.
If the meter beeps or gives a reading close to 0, the box and the load center are electrically connected. This means there is a proper grounding conductor installed. If the meter does not beep or has a reading of infinity, the box and the load center are not electrically connected. You'll have to install an approved grounding conductor throughout this circuit, if you want proper grounding.
Checking Continuity to a Known Good Ground
If you have a known good ground nearby (from another circuit, for example), you can use this ground to test for an equipment ground at the box in question.
- Set your multimeter to the continuity setting or the lowest resistance setting.
- Place one lead on the known good ground.
- Place the other lead on the junction box under test.
If the meter beeps or gives a reading close to 0, the box and the known good ground are electrically connected. This means there is a proper grounding conductor installed. If the meter does not beep or has a reading of infinity, the box and the known good ground are not electrically connected. You'll have to install an approved grounding conductor throughout this circuit, if you want proper grounding.
Check Continuity to the Grounded Conductor
If neither of these options are available, the next best option is to check for continuity between the box and the circuits grounded conductor (neutral). These two conductors should be electrically connected (bonded) at the main service panel, so checking continuity between them can (usually) determine if there is an equipment ground.
WARNING: This method relies on the circuit being installed correctly. If the grounded conductor (neutral) is (incorrectly) connected to the grounding conductor anywhere along the circuit, this test may give invalid results.
- Set your multimeter to the continuity setting or the lowest resistance setting.
- Place one lead on the grounded conductor (neutral).
- Place the other lead on the junction box under test.
If the meter beeps or gives a reading close to 0, the box and the grounded conductor (neutral) are electrically connected. This means there may be a proper grounding conductor installed. If the meter does not beep or has a reading of infinity, the box and the grounded conductor (neutral) are not electrically connected. You'll have to install an approved grounding conductor throughout this circuit, if you want proper grounding.
NOTE:
All continuity testing should be carried out while the circuit is dead. Shut off power to the circuit at the breaker before working on the circuit, and verify the circuit is off using a non-contact voltage tester.
Electricity is dangerous and can lead to property damage, injury, and death. If you do not feel comfortable working with electricity, please contact a qualified Electrician.
That does indeed describe a properly engineered 50 amp device.
It is normal for appliances to use slightly lighter gauge wire than would be used in building wiring. You can observe that inside electric ranges, dryers, and water heaters, where you will see the 10 or 8 gauge incoming supply wires to a terminal and then 12 or 14 gauge wire going from the terminal block off to the components.
Because the wire is inside an enclosed box, and is not tightly bundled or surrounded by thermal insulating materials, its elevated temperature will not cause any danger. It will run a little warm at peak current, but be far below "hot". The same is not acceptable inside dwelling walls were it will be in contact with wood, fiberglass, cellulose insulation, etc.
As for standards, I have determined this is beyond the scope of the NEC and falls into the domain of the National Fire Protection Association (NFPA) standards. That seems to cost $$ to view.
Best Answer
Assuming that it's twin and earth wiring (which it sounds like from your description), yes the earth wire in the cable is typically uninsulated once the outer sheath has been removed. It's usual to use a piece of yellow and green sleeving to slip over the earth wire to provide basic insulation.
I'd recommend that you run the outer sheath of the cable into the junction box, or you could likely run into water ingress issues in the future.
As to why it's exposed, I'd hazard a guess that it's a cost saving measure to avoid the additional insulation. Except in a fault condition, there should be no current in or potential on the earth conductor, so it doesn't need the same level of protection as the line conductors.