Electrical – Is it possible to make space for a double-pole breaker in this panel

circuit breakerelectrical-panelsubpanel

I need to add a 90A double-pole breaker to the service panel on my house to feed a subpanel in a detached garage. It is a GE that uses Q-line breakers. Looking at the current layout, I'm not sure it can be done. I've had a few electricians say it is possible to make room, whereas others have indicated a subpanel is needed next to this one.

service panel

It looks like there is a half-space available under the heat pump breakers. I was considering replacing the dishwasher and microwave breakers with a 15A tandem breaker, but this would only free up 1.5 slots total. The full size breakers in the upper left portion are AFCI. I don't think I can replace these with tandem breakers and still remain in code even if I replace the receptacles with the AFCI type.

Is there any way to accomplish this without needing to add a subpanel?

Best Answer

Ah, the tricky GE Qline.

  1. Convert the dishwasher to a 1-pole double-stuff breaker set low in the space.
  2. Pop off the cover above it. Now you have 1 space but it's a half space off-beat.
  3. Get a unique Qline double-stuff 2-pole 30A breaker, that is 1" wide and made to go in off -beat spaces. (And they require the off-beat, they can only work there).
  4. Move the water heater to that breaker.
  5. Voila, 2 full spaces freed. Use that for your 90.