My 5.8kw ceramic hob has been wired into a 30 amp junction box with the electric ignition cable of the old gas hob and then wired into the cooker switch with .6 mm cooker cable. Is this correct wiring?

Best Answer

I Forgot about this one. 5.8KW on a 240V would only draw a little over 24 amps. in the U.S. this would require 10 Awg wire. A standard wire type THHN 10 Awg crosses over to 4.166 MM as the aprox diameter as listed in the NEC chapter 9 Table 5. I am surprised the cable is not melting this is way under sized. To answer the question: No it is not correctly wired.