Electrical – Is the max current draw of wall outlets reported in RMS or peak

electrical

In the United States, the voltage of typical wall outlets is 120 Vac (RMS). Maximum current draw is 15 A or 20 A. Is this "maximum" expressed in terms of RMS or peak? The "maximum" seems to imply peak.

Extension to this question: If I plug multiple devices into a power strip with a 15 A fuse, should I be worried about the total peak current or total RMS current of the devices?

Best Answer

Like Brian said, it's measured in RMS.

For the extension: RMS again. For fast-blow fuses, the current rating is the maximum current guaranteed at which the fuse will not blow. But the fuse won't immediately blow at 15.1A -- the time vs. current graphs are provided for most fuses. Here's an example:

Average Time Current graph

As we can see, a 15A fuse is guaranteed not to blow at 15A. As the current increases, the time it takes for the fuse to blow decreases. A 15A fuse may take a minute to blow at 20A, but 0.3 seconds to blow at 30A.

Even though your 15Arms current is actually over 21A peak, the time that it goes above the 15A rating (~4ms per half cycle) is not sufficient to blow the fuse. Due to the fuse's thermal inertia you may want to derate the curve a bit, but at 15Arms you should be fine.