Electrical – Is this 240V outlet undersized

240velectricalelectrical-panelreceptacle

Garage has 100A service sub-panel from main home. The panel contains a 40A 240V breaker. This connects through a heavy-gauge wire (looks to be same wire as feeding the 100A panel itself) to what I think is only a 15A outlet. That is, based on the physical dimensions and prong arrangement compared to info I found online, I believe this is a NEMA #6-15R receptacle. Am I right?

If the rest of the circuit is 40A but the outlet 15A, then I think this would be undersized and dangerous? Would it be appropriate to replace this #6-15R with a #6-30R? Do I also need to put in a 30A breaker?

The reason this came up is that I would like to use a 20A 240V heater in the garage. The heater uses a #6-30P plug, which can be seen dangling in one of the photos below. Basically, I am looking for a safe way to clean up the electricals, in a way that will make the end result compatible with this NEMA #6-30P heater.

enter image description here

enter image description here

enter image description here

enter image description here

enter image description here

enter image description here

enter image description here

Best Answer

Change the 2-pole breaker to a Square D Homeline 30A breaker ($9). Make sure that cable is at least 10 AWG (8 or 6 will do).

Then fit a NEMA 6-30 as you intend.

Then replace those two 15A 1-pole breakers with Square D Homeline 15A breakers. If they power one cable with a shared neutral, use a 2-pole breaker.

Those Siemens QP breakers have no business in your panel. Donate those to someone with a Siemens/Murray panel. This isn't brand loyalty, the breakers do not fit properly and will arc.