Since the neutral and ground are isolated in a sub panel, is wiring a 240 volt heater from a sub panel different from wiring it to the main panel?
Electrical – Is wiring a 240 volt heater from a sub panel different from wiring it to the main panel
electricalheatersubpanelwiring
Related Topic
- Wiring – installing sub panel in garage off of house main
- Electrical – Wiring 100-amp sub-panel for 1hp pool pump and heater
- Wiring – main breaker panel to sub panel
- Electrical – Adding sub panel, odd main panel configuration
- Electrical – Sub-panel wiring, grounding, disconnect
- Wiring from basement main panel to garage
- Electrical – How should a sub panel be grounded if next to the main breaker
Best Answer
No, as long as you land the ground wire on the ground bus of course -- but that's a caveat when wiring anything to a subpanel. (I'd run it using /3 NM so that there's a neutral run to the heater in case it's needed for outlets on a baseboard setup or something like that...and in that case, you also have to remember to land the neutral wire on the neutral bus, but again, that's just like any other circuit.)
The hots hook up just like any other 220V circuit.