As seen in the picture, I have a live junction box that is partially covered by a wall in a closet. There is no light in this closet, so would be a great opportunity to add one. Was thinking I could add a simple round ceramic pull cord fixture, but don't think it will work given the obstruction. Also, would be ideal, to somehow relocate the fixture (higher) given the box is only 5 feet off the ground. Thoughts?

UPDATE and FURTHER CLARITY:
There is both BX wire (metal conduit containing hot/neutral) and NM going to the box with corresponding wires nutted. I'm not sure how responder is certain the ground wire is ungrounded, so that is first question. Other questions:

  • It looks like the BX armor is not in contact with the box, so ground would need to be the ground wire in the NM bundle?
  • Is there a way to add a light fixture to this box by perhaps cutting part of the drywall to allow to physically fit? Would this be a good idea? There would certainly be a bumping hazard.
  • As mentioned, ideally I would want to move the light above closet door or to the ceiling. I believe sufficient information has been provided to this end for now.
  • If I choose to simply cover, why does it need to be a metal cover? Added strength given it extends out from wall?

UPDATE #2: New picture attached showing wires heading to box.

UPDATE #3: For now, I have covered the box and will be adding a battery-powered light (if anything).

New picture
light fixture box

Best Answer

I have three things to tell you.

  1. That can't possibly be a legal installation. Junction boxes must remain accessible and cannot be walled up. Even partially covering one like that is going to cause the inspector to plotz. Also, it's obviously a NM extension to a knob-and-tube circuit, which is no longer allowed in most venues. Plus, even if it's legal, you have an ungrounded fault ground wire and no place to ground it. Whatever that NM leads to may appear to be grounded which is a dangerous deception.

    The reason I think the NM ground wire is ungrounded is because I assume the power is coming into the box via the older cable, since newer cable is usually used to physically extend a circuit. However sometimes newer cable appears between the service panel and older cable, so OP should disconnect the hots and test with a volt meter.

  2. I am not a licensed electrician so my advice may raise some eyebrows. I think you can add a light to the closet without substantially increasing the danger to your home and person. Screw a metal hex box to the ceiling of the closet and mount the pullchain light on that. Connect the ceiling box to the existing box with plastic conduit, and pull two wires to connect the lamp to the wire nuts in the existing box.

    Use the proper fittings to connect the conduit to the boxes. You'll have to knock out one of the openings in the existing box. You may want to use larger wire nuts to accommodate the three wires. Try to figure out the gauge of the wires in the existing box and size your new wires to match them; this helps protect some future occupant who might plug a toaster into your light fixture.

    I would use a needle-nose pliers to wind that bare ground wire into a small coil, and wrap some tape around it to keep it from touching the metal box. This eliminates one way to get a shock if some appliance on that NM cable goes bad. Then, close up the existing box with a proper metal cover plate and try not to think about it.

  3. Many licensed electricians post answers and advice on this site. If they disagree with me, you should listen to them. I tend to give advice consonant with how I maintain my own house, and I may be taking more risks than you would be comfortable with.