I have two main hot legs coming into my circuit breaker. One has a steady voltage of ~124V load or no load. The other has some mysterious problem. Sometimes it works fine delivering proper voltage under load. Other times it will drop to at or nearly at 0V under load. When all circuits on the low voltage leg are switched off the voltage will swing from 0V to a large reading. It will keep swinging for about 10 seconds until it finally stabilizes at 124V. I've taken each circuit, except for the 240V circut for the AC as it's winter and never turns on, and moved them to the good line and they all work fine. The utility company came twice and each time they left a note saying everything on their end is working.

What could be causing this?

Best Answer

It sounds like you have a bad connection or a broken wire somewhere upstream of your main breaker. Assuming that the power company's test were valid, then the problem would be the wire between your main breaker and the power meter. Other possibilities are that your main breaker is bad, or that the meter, meter box, or something upstream of that is broken.

See my answer to Insufficient voltage to dryer receptacle; what next? for why broken wires or breakers can cause weird voltage issues.