electrical-panel

I have an office in a building supplied with 3 phase electricity in the United States. There are several standard household 120V outlets in my office, each connected to a dedicated, 20 amp circuit with an 80% rated breakers. Assuming I will plug in an appliance continuously with a power factor of 1, am I correct in assuming that each receptacle on one of these dedicated circuits will support up to a maximum of 120V x 20A x 1PF x sqrt(3) x. 80 = 3325.5 watts? Or is it standard to somehow downgrade the electricity to single phase 120V when the 208V comes through the panel, effectively eliminating the square root of 3 term in my calculation above,leaving a maximum wattage of 1920? Thanks.

Best Answer

No. You don't multiply by the square root of 3 unless you're drawing all 3 phases in a delta configuration, and then, you multiply the pole-pole voltage (208) not the pole-neutral voltage (120).

When dealing with a single phase of wye or split-phase, it's exactly what it says on the tin:

120V x 20A x PF1.00 x 80%. 1920W.