Is there any minimum distance required between a junction box and copper water pipes? This is in an exposed basement ceiling and the box is near a couple of 1/2" water lines. There is currently about 5" spacing.
Electrical – Minimum distance from a water pipe to a junction box
electricalwiring
Related Solutions
Since there are slight differences depending on what type of communications systems we're talking about, we'll have to look at a few different sections.
NEC 2008
Article 800 Communications Circuits
800.44 Overhead Communications Wires and Cables.
(A) On Poles and In-Span.
(4) Clearance. Supply service drops of 0–750 volts running above and parallel to communications service drops shall have a minimum separation of 300 mm (12 in.) at any point in the span, including the point of and at their attachment to the building, provided the non-grounded conductors are insulated and that a clearance of not less than 1.0 m (40 in.) is maintained between the two services at the pole.
Article 810 Radio and Television Equipment
810.13 Avoidance of Contacts with Conductors of Other Systems. Outdoor antennas and lead-in conductors from an antenna to a building shall not cross over open conductors of electric light or power circuits and shall be kept well away from all such circuits so as to avoid the possibility of accidental contact. Where proximity to open electric light or power service conductors of less than 250 volts between conductors cannot be avoided, the installation shall be such as to provide a clearance of at least 600 mm (2 ft). Where practicable, antenna conductors shall be installed so as not to cross under open electric light or power conductors.
Article 820 Community Antenna Television and Radio Distribution
820.44 Overhead Coaxial Cables.
(B) Lead-in Clearance. Lead-in or aerial-drop coaxial cables from a pole or other support, including the point of initial attachment to a building or structure, shall be kept away from electric light, power, Class 1, or non–power limited fire alarm circuit conductors so as to avoid the possibility of accidental contact.Exception: Where proximity to electric light, power, Class 1, or non–power-limited fire alarm circuit service conductors cannot be avoided, the installation shall be such as to provide clearances of not less than 300 mm (12 in.) from light, power, Class 1, or non–power-limited fire alarm circuit service drops. The clearance requirement shall apply at all points along the drop, and it shall increase to 1.02 m (40 in.) at the pole.
Article 830 Network-Powered Broadband Communications Systems
830.44 Aerial Cables.
(C) Lead-in Clearance. Lead-in or aerial-drop network-powered broadband communications cables from a pole or other support, including the point of initial attachment to a building or structure, shall be kept away from electric light, power, Class 1, or non–power-limited fire alarm circuit conductors so as to avoid the possibility of accidental contact.Exception: Where proximity to electric light, power, Class 1, or non–power-limited fire alarm circuit service conductors cannot be avoided, the installation shall be such as to provide clearances of not less than 300 mm (12 in.) from light, power, Class 1, or non–power-limited fire alarm circuit service drops. The clearance requirement shall apply to all points along the drop, and it shall increase to 1.02 m (40 in.) at the pole.
tl;dr.
Telephone (Communication Systems)
- 12" (300 mm) at any point of the span.
- 12" (300 mm) at the point of attachment.
- 40" (1 m) at the service pole.
Antenna (Radio and Television Equipment)
- Kept away if possible.
- Should not cross over or under.
- 2' (600 mm) if proximity can't be avoided.
Cable (Community Antenna Television and Radio Distribution)
- Kept away if possible.
- 12" (300 mm) if proximity can't be avoided.
- 40" (1.02 m) at the service pole.
Broadband (Network-Powered Broadband Communications Systems)
- Kept away if possible.
- 12" (300 mm) if proximity can't be avoided.
- 40" (1.02 m) at the service pole.
There is no minimum distance specified in the NEC. It can be as close as is physically possible given the constraints of framing, trim, etc. There's several rules about maximum distance and spacing and when to include door swings or not, and what constitutes a usable wall requiring outlets in the first place. But no minimum.
Now, conceivably, someone could interpret that since the outlet is within 6 feet of a "damp" area (patio) that it may need to be GFCI protected. I personally believe this stretching the intent of the NEC too far since the theoretical appliance in a damp area would have it's cord running through an open exterior door into a different room.
There could be other requirements by Washington state or your local jurisdiction. The NEC is mute on this matter, but you should inquire with your local building authority to be absolutely sure there are no other applicable requirements or "creative" interpretations of GFCI requirements.
Related Topic
- Electrical – New junction box, or pigtail within receptacle
- Electrical – Light junction box near water
- Electrical panel grounding
- Wiring – Mystery Romex in junction box
- Electrical – Minimum Distance from Receptacle Terminal to Conduit Connector
- Junction Box Wiring – How to Remove a Cable from a Junction Box
- Electrical Subpanel – Minimum Distance Between Main Panel and Feeder
- Attic Wiring – Adding a Junction Box in Attic for Ceiling Box Congestion
Best Answer
Hmmm... Assuming, from your use of 1/2", that you are in North America, it's actually something that people argue about (in the US anyway). Here is how the NEC reads in Article 110.34, Work Space and Guarding:
The argument is in the interpretation of "Service Equipment" when it comes to residential panels. If the panel is a "sub-panel", meaning NOT the first place where the utility feed lands, then some people say this rule does not apply. Other inspectors do not make the distinction.
Then, there is the term "... in the vicinity of...", because it doesn't state a distance. In a previous portion of the same article, they call out for 3ft clearance as "working space", but some inspectors interpret that to mean only IN FRONT OF the gear.
Then there is the phrase "... or whose malfunction would endanger the operation ...". Is a 1/2" water pipe likely to burst and spray on a load center?
My best advice is to as a local inspector, they are the final say-so.