I recently added some ceiling lights and had to tap into an existing junction box that had a 3 wire multiwire branch circuit run to it. This is a kitchen GFCI receptacle. The red wire is on a breaker that runs to the dishwasher/garbage disposal. The black wire fed the GFCI (all share neutral and ground). I pigtailed off the black to feed power to the lights. My question is should all neutrals be pigtailed – including the one run from the GFCI to the downstream outlet (GFCI protected)? Does the attached diagram look correct? Should the neutral going to the GFCI protected outlet (off the GFCI) be pigtailed with the rest? I excluded the ground wires from the diagram – they are all pigtailed together.
Electrical – Multiwire Branch Circuit with GFCI
electricalgfci
Related Topic
- Electrical – How to replace circuit breakers with GFCI breakers when it is a multiwire branch circuit
- Electrical – a multiwire branch circuit
- Electrical – GFCI protection for multiwire branch circuit in shipping container workshop
- 110v outlet on 220v circuit with 220 GFCI to boat dock
- Installing GFCI outlets in multiwire branch circuit
- GFCI outlet trips overnight. The breaker indicates there is ground fault. Outlet tester shows no lights (no power?)
- Electrical – Is it possible to wire 2 GFCI receptacles on 2 circuits with 12/3 wire shared neutral
- Electrical – Is this how I add GFCI and Regular Outlet to existing Multi Wire Branch Circuit, 20amp? 12/3 to 12/2 wiring with GFCI
Best Answer
No, do not join all of the neutrals. The GFCI load terminals need the neutral to remain separate. Your diagram is correct in that respect.