Electrical – Need Comment on How the House Was converted from 120vac to 240vac

electrical-panel

This is an As-built drawing of how my home was converted from 120vac to 240vac
The house now has the Neutral moved in the house and used as L2 power source
Each circuit had the neutral moved from the Neutral bar and attached to a breaker on the L2 side. Now the circuit has L1 and L2 load making 240vac.
Ground wire is connected to the outlets and lights so we have to be careful not to get between the Ground and L1 or L2 load wire. It has been working for 15 years now.

Note we are not in USA and in an isolated area with no inspection and rules.
Just wanting to check, knowing the safety concern with the ground and possibility of electrical shock what other concerns might be known.

enter image description here

Best Answer

You should change the light switches to double pole switches that cut both halves of the power supply. These are commonly available (how hard they are to get where you are, I don't know.)

The breaker handles for each pair of circuits (that are now "one") should be "tied" if the breakers are not themselves double breakers (which is what I think you've described) - preferably they would all be replaced with double-pole breakers which do not need a tie. While you don't have local codes/inspections, this would be safest for you. This requires the pair of breakers to be located side-by side, not opposite as you have drawn.

You should also change the outlets (evidently still US-120VAC style) to the local common/standard 240VAC style, if only to prevent mishaps with 120VAC equipment being plugged in.