I'm getting ready to install a nema 14-50 outlet for an electric car/vehicle (EV) and I'm looking at the details. I found out that NEC 2017 section 314.17 talks about enclosures but I'm a bit confused.
The outlet will be in my (attached) garage so it would be indoor. I'm planning to run NM-B cable (AWG 6 or 8, about 15 ft inside drywall) from the breaker box (upstairs) where I'll have it connected to a 40A breaker. I can't do 50A breaker because my SE cable is rated at 75A and the main breaker is 60A. The city permit people had no problem with this when I consulted them. I can use it at night when nothing else is being used.
Do I need a metal box for the outlet? Will attaching the cable to the stud within 8in of the box be required? Am I missing any other details?

Thanks

Best Answer

I'm betting this is a Tesla charger, which draws 40A. You cannot load a 40A breaker at 40A continuously (defined as 3 hours or more), you can only load it to 32A (80%) because technically, a 40A breaker is designed to protect 40A rated conductors, which by code must be sized at 125% of the continuous load. So you need conductors rated for 50A and a 50A breaker, it wasn't a suggestion on their part. If you ran #6 conductors and wanted to protect them with a 40A breaker, technically that would not violate Code, but you are likely to have nuisance tripping of that breaker. That's a nasty surprise to find out about in the morning when you want to drive to work...