I'm wanting to use a 220v, 50Hz, 6000w Infrared Flash Dryer but don't have a way to power it currently… Additionally, the appliance comes without a plug… just 3 wires ready to be connected to a plug.

I've done some research and figured out that I should be using a 30amp breaker with #8 wire (it'll be more than 25ft from the box).

How do I know what receptacle and plug to use? I read that NEMA 10 is typically used for clothes dryers and stuff and that I should be looking at NEMA 14, but it has 4 prongs and the appliance only has 3 wires… 🤔

If you suggest NEMA 10, would it hurt to go with NEMA 14? If I were to use NEMA 14, would I ignore the ground or the neutral when adding the plug onto the appliance?

Best Answer

Can't speak to if the frequency will be a problem, but 240V plus ground is a NEMA 6. Do not use a NEMA 10, it is two hots and a neutral.

I don't believe a flash dryer operates at full current for 3+ hours, #10 and a 30A breaker should be fine, if it operates more than 3 hours at full current then #8 copper wire and a 40A breaker would be needed.

Edit: After good night's sleep and a cup of coffee I realized my answer at very least violated NEC 210.21 which limits cord connected loads on a 30A circuits to 24A, you would need to use #8 copper, a 40A breaker, and a NEMA 6-50 (or a NEMA 14-50 which would probably not satisfy a strict interpretation of (UL) Listing requirements of the cord cap to only install as the instructions describe and as tested by the testing agency, but (UL) is probably thrown out the window using a 50Hz appliance that has 50Hz sensors, timers or relays on 60Hz).