To answer all the issues you raise would require a book on US electrical wiring. Or several. And a copy of the Code.
The vast majority of outlets in residences in the US are attached to branch circuits that are rated at 15 Amps and 120 Volts. Current practice and code calls for outlets like these
![outlet](https://i.stack.imgur.com/puTzV.jpg)
This version is tamperproof, required in many jurisdictions. The non-tamperproof look similar, but the slots do not have internal baffles
You may see different styles, such as Decora, or decorator style, which are functionally identical to basic outlets, but have a rectangular face
![decora outlet](https://i.stack.imgur.com/Ym1hX.jpg)
20 Amp circuits generally require slightly different outlets (if you are going to draw the full 20 Amps or there is only one outlet on the line) like these
![20a outlet](https://i.stack.imgur.com/Bymwl.jpg)
But you can also find the lower 15 Amp outlets on circuits that are properly wired for 20 amps. Obviously 15 Amp outlets are limited in use to 15 Amp appliances, even if they are on a 20 Amp line.
Certain locations, especially where there is a risk of moisture, such as bathrooms, require a ground fault interruper (GFI) type outlet
![gfi outlet](https://i.stack.imgur.com/LCOti.jpg)
These also come in tamper resistant and 20 Amp versions and vary like the basic outlets.
All of the above are grounded outlets, required in almost every jurisdiction for new construction and renovations. Some older installations may have ungrounded outlets.
![ungrounded outlet](https://i.stack.imgur.com/4YtXu.jpg)
These generally cannot be used except as a direct replacement for an existing one, and even then setting up a properly grounded outlet is preferred and may be required.
All of the 120 Volt outlets require a hot wire (usually black or red) and a neutral wire (always white). Grounded outlets also require a ground wire (green or bare). Outlets can be always live or switched. Live outlets have the hot wire coming directly from circuit without interruption. Switched outlets have the hot wire going through one or more switches before reaching the outlet so that the power can be turned on or off.
All of the 15-20 amp outlets shown above are duplex, that is there are two receptacles for plugs on each. These almost always are bonded together by a strip of metal. When you wire to one, both are energized. This bonding strip can be broken off allowing each of the receptacles on the outlet to be powered separately. This is most often done to allow one receptacle to be always live and one to be switched. This also allows each receptacle to be on a separate branch circuit (for heavy power use).
Some residences use higher amperage outlets for large appliances, such as an electric stove or dryer, and the outlets vary base upon a number of factors. Examples can be seen in the chart linked in the question.
Similarly, some residences use 240 Volts for large appliances and wells, and the outlets also vary considerably, and can be seen on the linked chart.
This is a very brief summary of the type of outlets most commonly seen in US homes. The full range of outlet types and uses is beyond a simple summary. The range of possible switching and wiring configurations also is nearly infinite. But this site welcomes questions on any particular configuration or problem you may encounter, so ask away.
Best Answer
Can't speak to if the frequency will be a problem, but 240V plus ground is a NEMA 6. Do not use a NEMA 10, it is two hots and a neutral.
I don't believe a flash dryer operates at full current for 3+ hours,
#10 and a 30A breaker should be fine, if it operates more than 3 hours at full current then #8 copper wire and a 40A breaker would be needed.Edit: After good night's sleep and a cup of coffee I realized my answer at very least violated NEC 210.21 which limits cord connected loads on a 30A circuits to 24A, you would need to use #8 copper, a 40A breaker, and a NEMA 6-50 (or a NEMA 14-50 which would probably not satisfy a strict interpretation of (UL) Listing requirements of the cord cap to only install as the instructions describe and as tested by the testing agency, but (UL) is probably thrown out the window using a 50Hz appliance that has 50Hz sensors, timers or relays on 60Hz).