There is a provision in the National Electrical Code that will allow a 3-wire installation, in situations where there is existing wiring (250.140 exception). You should be fine to install a three prong receptacle, and use a three prong range cord.
There should be special instructions in the manufacturer's installation instructions that are included with the range, that will specify exactly how to attach the 3-wire cord.
If you're really concerned about it, or want to update to follow modern code. You could install a new 3-wire with ground cable, and use 4-prong receptacle and cord.
National Electrical Code 2014
Chapter 2 Wiring and Protection
Article 250 Grounding and Bonding
250.140 Frames of Ranges and Clothes Dryers. Frames
of electric ranges, wall-mounted ovens, counter-mounted
cooking units, clothes dryers, and outlet or junction boxes
that are part of the circuit for these appliances shall be
connected to the equipment grounding conductor in the
manner specified by 250.134 or 250.138.
Exception: For existing branch-circuit installations only
where an equipment grounding conductor is not present in
the outlet or junction box, the frames of electric ranges,
wall-mounted ovens, counter-mounted cooking units,
clothes dryers, and outlet or junction boxes that are part of
the circuit for these appliances shall be permitted to be
connected to the grounded circuit conductor if all the following
conditions are met.
(1) The supply circuit is 120/240-volt, single-phase,
3-wire; or 208Y/120-volt derived from a 3-phase,
4-wire, wye-connected system.
(2) The grounded conductor is not smaller than 10 AWG
copper or 8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded
conductor is uninsulated and part of a Type SE serviceentrance
cable and the branch circuit originates at the
service equipment.
(4) Grounding contacts of receptacles furnished as part of
the equipment are bonded to the equipment.
Your panel needs to be reviewed, carefully.
When you do, you'll have no trouble finding 2 spaces.
It's a quality CH panel, albeit with only 20 spaces. I'm not counting the top 2 spaces in each row, which collectively are the main breaker (100A). Good news is, with this panel arrangement, if you shut off the main breaker, everything is cold except those conspicuous large screws. Which makes it more DIY-friendly than most.
I see seven 240V breakers tying up 14 of 20 spaces. That means all 120V loads in the entire house are served by six 120V breakers, which is pretty compact. I don't believe a house can have seven 240V loads. The usual big four are dryer, A/C, water heater and oven. So I suspect many of these breakers are surplus, particularly since they're off.
The only conceivable reason for this many 240V breakers is having all-electric heat, e.g. baseboard, and if that's the case, forget about an electric range/oven - you just don't have enough service.
Two of those 240V loads are 120/240 split phase. The right side middle rows are a 30A breaker, and looks to have the heavier 10 AWG wire, so it looks to be a dryer. The left side 4th and 5th from the bottom is weird because the white wire is being used as a hot, and the red wire is taped white and used as a neutral (which is illegal to do). That's not right. It might be a multi-wire branch circuit or MWBC, serving two 120V circuits, but I doubt it.
I see a red wire that's taped off, that means there's another black-red-white cable with black and white only being used. That seems weirdly sloppy (why use white for a 240V circuit when you have red) which only worries me more about the quality of work in general.
Even worse, look at the bottom right breaker. It's a 60A breaker but that's NOT a 4 AWG wire. It's either 12 AWG or maybe 10 AWG. That needs a 20A or 30A breaker, respectively. I know exactly what those breakers cost, so no excuse! SHUT IT OFF NOW. NEVER turn it back on. Replace with a 20 or 30A breaker respectively, most hardware stores stock CH220 or CH230. And if it trips, it's supposed to.
Other than that, Mrs. Lincoln...
Go through each circuit in the panel, for two reasons. First, to find any more defects -- after all, I could find two whoppers from a photo. Second, to understand what you do have, so you can either trim or consolidate and free up 2 breaker spaces.
Don't bother hunting down double-stuff (duplex/tandem) CH breakers. Yes, they exist, but you really, really need to re-evaluate this panel, given the large number of defects I've seen from one measly photo. And I think as you do so, you'll free up some space.
Oven/range is straightforward
You simply need a 50A breaker and 6 AWG copper (or 4 AWG aluminum). You could go 40A and 8 AWG, but the difference is only a few bucks, and you'll have a wider selection of ovens/ranges if you go 50A. CH 50A breakers are readily available, not quite as widely stocked as the 20/30s but any big-box should have them. You cannot reuse the 60A breaker.
However, cooking on electric kinda sucks, if you're coming from gas. It's a very annoying learning curve, and a lot of compromises and workarounds. Not recommended.
If you must upgrade the panel
CH is a fine system. One option is get a larger CH panel. However, if you replace the panel, you will need to upgrade most of all of your 6-8 120V loads to AFCI or GFCI or both/combo, and that could get costly. The disadvantage to CH or any 3/4" wide breaker is being smaller, there's less space to cram advanced tech, so they're more expensive or unavailable.
Don't go cheap. This panel is much better than the Homelite and other shlock the local big-box is shoveling. (You can't go by brand anymore, as good brands like Square D and Eaton have bought up cheapie sub-brands.) You have to ask for the good stuff. Get a top-shelf panel from a proper electrical supply. And go really big - bare minimum 42-space, 60-space is not too many. If the main breaker for such a panel is too large, bypass it - put a 100A breaker in the normal spaces and backfeed it (much like is occurring in this panel).
Best Answer
Yes, that is acceptable. You don't need a junction box at the service panel end. You can have a pigtail in the service panel. You also don't need another box for the oven. Just remove the existing receptacle, pigtail on some 12 gauge wire, and put in a standard outlet.
Keeping the 8/3 in place also allows for future replacement with an electric oven by swapping out the receptacle.