Electrical – On a typical US NEMA 5-15 outlet, what parts are generally safe to touch when it is live

electricalreceptaclesafety

I'm particularly curious if the yoke on typical outlets (e.g. NEMA 5-15) are safe to touch when the outlet is energized.

My understanding is the only way the yoke would be energized is if there is a short circuit somewhere (hot wire touching the yoke, or touching another conductor which touches the yoke) and the outlet is not properly grounded.

So in general, what parts of an outlet are safe to touch when it is live? Only the plastic? Plastic parts and the yoke?

Best Answer

If you don't touch anything else you can touch any part of it.

In order to be shocked or electrocuted you must have a complete circuit.

If I touch an energized conductor with one finger but the rest of my body is insulated or isolated then I will not be shocked because there is no complete circuit.

That said, the energized ungrounded conductor (hot wire) will shock you if you also touch the either the intentionally grounded conductor (neutral) or the equipment ground conductor (ground wire). The equipment ground should be connected to the receptacle yoke so touching that would also complete the circuit. Additionally, touching any metal piping system in the building or other metal parts of a building can also get you shocked.

The safest course of action is to de-energize the circuit, lock it out, tag it out, and then work on it.

Stay safe!