Your grounding problem is due to the open N-G bond in the service disconnect
An outlet tester's "open ground" indication is an indication of an open somewhere between the ground contact on the receptacle and the N-G bond in the service equipment, as the light in the tester that corresponds to this is connected from Hot to Ground, and if the bond is intact, that circuit will be completed, even if the grounding electrode system is missing altogether. However, if that Neutral-Ground bond's gone, that'd explain the open ground reading you see.
As a result of that, I suspect the grounding electrode system to the disconnect is not the source of your issue; note that the pool tech was correct in disconnecting the redundant GEC to the pool pump as the pool pump and pool bonding grid are bonded to the mains equipment grounding system through the pool pump circuit's equipment grounding conductor (if nothing else). The grounding electrode should still be examined while you have qualified eyeballs in there, though.
The busted RMC for the service is actually not the largest safety concern with your parents' electrical installation, though! That subpanel was made by Federal Pacific Electric, and is an outright fire hazard! Many of those breakers cannot be relied upon to trip if a circuit is overloaded (either due to common-trip jams or simple miscalibration), and the Stab-Lok design is prone to contact faults in the breaker-to-busbar connections as well, which can lead to fires within the panel itself. As a result, the only fix is to replace the entire panel with a new one.
So, the verdict is:
- Replace the FPE panel with something decent, see below for replacement suggestions
- Replace the disconnect with something decent since it's also a FPE atop having its guts rusting out on you -- note that it can be a different flavor than the subpanel
- Have the damaged RMC service conduit permanently repaired or replaced
Panel replacement options
There are two criteria I use when choosing replacement panel types:
- It needs to be available in >42 slots (42 is a bare minimum slot count for a main panel)
- It needs to be available in both single and three phase version (this is a sign of a commercial grade panel, not something that's purely builder/residential grade)
This leaves you with a few options, depending on what you can get (i.e. some supply houses are partisans to one manufacturer or another) and whether you can rip out the existing enclosure:
- Square D QO and Eaton CH are both considered "industrial grade" lines, but they are slightly costlier due to using a 3/4" form factor. They do allow you to get a better slot-to-space ratio, which is a factor if you're using an Eaton retrofit kit in the existing enclosure.
- Eaton BR is a midrange line (some would say it's builder-grade with industrial aspirations). It has readily available exotics and a good variety of options, while being inexpensive and widely distributed.
- Siemens (QP) is one of the few "industrial grade" 1" breaker lines
out there. It is less costly than a 3/4" form factor panel, while providing basically the same level of performance, and access to >42 slots.
- Last but not least, if you can't rip out the existing panel enclosure at all, Eaton has retrofit interiors available in both the BR and CH product lines that can be used in this application. You're limited on slot count by the existing enclosure, though, so this is kind of a last resort compared to putting in a new panel that will let you take advantage of the code changes over the past 15 years that liberalized panel sizing.
As to the service disconnect, it can be replaced with a type of device called an "enclosed circuit breaker" such as an Eaton ECC series if you reroute the swimming pool circuit to the new subpanel, or with a standard 200A loadcenter of some sort -- in fact, this'd be a perfect application for one of the small feed-through-lug equipped loadcenters Eaton makes, such as a BR816B200RF. That way, you don't need to burn 4 slots on a 200A subfeed lug in the outdoor panel, while the swimming pool circuit can stay routed the way it is. In addition, you may want to have the conduit rerouted so its not trying to drain water that gets in straight into the panel, or at least ensure that the new install has the top conduit fitted correctly so it isn't leaking water into the panel.
I had an instance in my current home where the previous owner replaced a three way switch with a non-3-way dimmer and it acted like your situation. The original switch would seem like it did not work, unless the dimmer was on, then it would switch the dimmer.
Take a look at the wires you have and also look at wiring diagrams for a three way light circuit and see if anything makes sense in that context. For my situation, I had to remove three light switches downstairs where the bad dimmer was and figure out what every single wire did until I found the two travelers and hot that were meant for the original three way.
For now, also check your breakers. It's possible that a certain on/off arrangement of your new switches is leading to a short that is tripping the breaker since it doesn't seem like you truly know what wire goes to what screw.
Best Answer
Install the chains to the light and to the mounting plate. Then weave the three wires through the chain up into the mounting plate. Connect the ground wire from the light to the ground from the mounting plate to the ground from the ceiling. Then connect black to black and white to white.