I generally do my own electrical work but needed to upgrade my service from 100A to 200A so I hired someone. I had them add some outlets to my garage while they were at it because I was feeling lazy.

Today I decided to add more outlets and noticed they used low voltage brackets rather than the enclosed junction boxes I always use. I am assuming this is a code violation, but before I complain I wanted to ask here. I live in California if that matters.

115V outlet through low voltage frame

Best Answer

What sort of joker did that?

Clearly, whichever joker did that needs to be sent back to their apprentice electrician's training, because line voltage connections need to be in a box! If you see them around again, be sure to thwap them upside the head with NEC 300.15 for me, OK? (P.S. none of the exceptions in 300.15(A) through (L) apply to this situation.)

300.15 Boxes, Conduit Bodies, or Fittings - Where Required. A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring.

Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed.

Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (L).