I have a US house built in 1958 that has been remodeled in many stages over the years. I recently tested a circuit that included ungrounded outlets in the old part of the house. A number of years ago, we remodeled a bathroom and had the electrician replace a couple of ungrounded outlets on that circuit with what were supposedly grounded outlets (with a GFCI thrown in). I checked both those outlets and there is a ground wire connected to the outlet and going into the wall.

My Sperry (plug-in) tester shows an open ground. Do these testers always show an open ground when a circuit doesn't have a ground back to the panel?

Another couple of notes/questions:

  • On one outlet, my Sperry non-contact tester lights up when I get close to it. This works as expected on other outlets (on other circuits). When I pull that outlet out of the wall and test the neutral and hot wires, hot lights up (as expected), neutral does not. Does this indicate a problem with that particular outlet unit or just the general unreliability of non-contact testers? My tester had the same result with two different outlets hooked up to these wires.
  • Going back to those "grounded" outlets mentioned above, a multimeter shows about 116V across hot/neutral, but zero from neutral/ground and hot/ground. That seems to indicate that despite the presence of a ground wire, that ground doesn't appear to actually be connected to anything. Is that a reasonable conclusion?

Best Answer

You're about correct on the ground wire being floating loose at the other end

The other end of that ground wire is indeed most likely floating loose; this is OK if the outlet is GFCI protected, though, as the GFCI will trip and save you if something plugged into it tries to bite you.

As to the NCV tester...

Since the neutral is bonded to ground at the main panel, a normally functioning neutral will not light up a NCV tester (you can test this by sticking the tip of the tester into the neutral slot on a normally wired outlet). It's neither a problem with the tester, nor the outlet.