Electrical – Paralleling 8-gauge wires in a 220 volt 66 amp circuit

electrical-panel

I hooked up a tankless heater, which draws 66 amps. (it is on a 70 amp breaker). The installation guide says to use 6 gauge wire.

I had a 4-wire circuit of 8 gauge that runs right past the room where heater will be (it went to a range; I have a gas range now). So I took the white and red wires together (paralleled), and put them on one leg. I put the ground wire (10 gauge) and the red wire (8 gauge) together, and put them on the other leg.

Am I correct that this will draw 66 amps? How will it split the current? Will each wire draw 33 amps or will the bigger 8 gauge wire (paralleled with the 10 gauge ground) draw more that the 10 gauge? Either way, I should be OK, correct?

It works fine; I grounded it through the old electric water heater circuit in the room, which had 10 gauge ground (like the 6 gauge cable they said to use.)

Best Answer

I heat S-16 requires a 70 amp breaker (it has internal sub breakers) this unit requires 240v at 66.6 amps. This requires a 240v breaker with L1, L2, neutral, and ground to properly operate using #6 copper according to the rep I talked to. Connecting any other way will not work at the rated 16Kw. (888)818-4328