Electrical – Pigtail off before kitchen 20A GFCI for Cabinet Lighting

electricalgfciledreceptaclewiring

I'm struggling finding a power source for the cabinet lighting in our remodel. The breaker box is very full and I'd rather not re-wire/double up breakers are this time.

Is it ok to pigtail off of one of the LINE inputs of a 20A kitchen GFCI?

These are all LED lighting, which I've read about the issues with GFCI cicruits and LEDs on the load side. Hence, pigtail off of the LINE side.

It would be fed into a metal 4×4 box and conduit.

Best Answer

No. A circuit which supplies kitchen countertop receptacles can ONLY serve:

  • Receptacles located in the kitchen or dining area
  • A clock on the wall (remember those)
  • Auxiliary electrical loads in a gas powered oven/range

Even if your installation is grandfathered, you're not allowed to make a grandfathered installation worse than it already is.

However, kitchen receptacle circuits can certainly serve receptacles in the kitchen under or near a cabinet. Are you sure that low-voltage LED lighting doesn't come with some sort of power supply that plugs in?