It is not controlled by a switch and I didn’t break any tabs.
What could make this happen?
- Debris inside the socket of the ground conductor
- A defectively manufactured outlet
Is it safe to use the outlet or just the bottom of the duplex?
Safety is a relative thing.
If you use the ungrounded top outlet it will be as safe as older houses that were built before grounding was a thing, and were considered safe in their time. It will also make no difference for two prong appliances.
If you crazyglue an outlet protector over the top outlet to prevent use of the top outlet, then it will be as safe as not using it.
But maybe the DC converter will short to hot and electrify the phone someone is holding up to their head.
I say take it back to the store and report the fault and get an exchange.
You got a product that is less than it should be. Safety or not, you'd return a plasma tv if it had lines down it or only received even channels. Return this outlet too.
Do outlets with USB ports show open grounds?
Only busted ones.
would putting a GFI outlet in that box assure it is grounded?
Nope. GFCIs do not create ground.
Changing the part out (with a gfci, or with any other outlet) would most likely solve the problem though. And in a kid's room, I think a GFCI is worth more than USB outlets if its a kid you want to keep.
Perhaps consider installing one GFCI in the "first" outlet box in that room, or in what ever the next closest junction before the circuit enters that room. Then USB outlets inside the room. In 60 seconds of Googling, I could not find an outlet that had GFCI and USB in one. You could also use a GFCI breaker but those are a pain in the neck.
something I may be missing
The receipt for that usb outlet, and its original packaging? With that, you should be all set. Let the clerk know it is dangerously faulty so they think longer before re-shelving it. If you get another of the same model and it has another fault, then you should tell us what model it is so it can be avoided. Good on you for testing the outlets after installing. I haven't done that on nema 5's in a while....
My concern here would be for physical abuse
Right now, nothing stops those NM cables from getting whacked/pinched/crushed with books and such, especially if you have heavy tomes on your shelves. This could be considered a violation of NEC 334.15(A) or (B):
334.15 Exposed Work. In exposed work, except as provided
in 300.11(A), cable shall be installed as specified in 334.15(A)
through (C).
(A) To Follow Surface. Cable shall closely follow the surface
of the building finish or of running boards.
(B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal
conduit, intermediate metal conduit, electrical metallic tubing,
Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means. Where passing through a floor,
the cable shall be enclosed in rigid metal conduit, intermediate
metal conduit, electrical metallic tubing, Schedule 80 PVC
conduit, Type RTRC marked with the suffix -XW, or other
approved means extending at least 150 mm (6 in.) above the
floor.
Type NMC cable installed in shallow chases or grooves in
masonry, concrete, or adobe shall be protected in accordance
with the requirements in 300.4(F) and covered with plaster,
adobe, or similar finish.
You have two options to address this
There are two ways to address this issue: you can either replace the NM cables with a wiring method better suited to withstanding said reader-inflicted physical abuse, or you can put something in that will protect the boxes and cables from rough encounters with books while still allowing for access to them. We'll discuss these options in turn.
Making this more rugged
While the normal wiring methods that are used to withstand the NEC's definition of "physical damage" are the various flavors of heavy-duty rigid conduit (RMC, IMC, EMT, Schedule 80 PVC, and RTRC-XW), surface metal raceway is also rated for such a duty, and doesn't suffer from the bending radius issues that other wiring methods in this application would have to deal with.
If you're using Legrand's Wiremold line for this, you'll need:
- Two BW17 right angle raceway-to-1/2" conduit fittings, attached with 1/2" chase nipples and locknuts
- Two BWH6 flat elbows
- A BWH7 inside elbow
- A length of BWH1 raceway
- And a two gang metal extension ring for the old switch box
The idea here is that you use the extension ring instead of the normal starter box (as they don't make one in two gang, and two-gang to one-gang mud rings stick out too far) along with one of the BW17 fittings and associated parts to get the raceway going upward from the gang furthest from the inside corner, then use the two flat elbows and the inside elbow to get around the bend and going back down. Then it's just a matter of using the other BW17 and its friends to transition the wires back into the box.
Once the raceway's in, then, you run individual THHN wires inside it to connect the circuits between the two boxes, just as if you were working in conduit. (The existing NM cables can be tossed, or shucked and their wires kept for pigtail duty, your choice.) Don't forget to plug the knockouts where the cables once entered/exited the boxes!
Using some cabinetry to box the boxes
If you feel yourself a better cabinetmaker than electrician, another option for this situation would be to put a cabinet divider wall in just to the right of this, and then add a cabinet door over the front, maintaining access while protecting the existing assembly from physical abuse or damage. This also has the advantage of being a more finished look, at the cost of having an "un-cabinet" in your house that you can't really use for anything at all. Making it match the existing built-in bookshelves may be a challenge, as well.
Best Answer
If the clamp breaks off, strictly speaking, the box is trash and should be replaced. In practice, there's usually a little latitude.
(I prefer metal boxes.)