Electrical – Potential Home Grounding Issue – Illinois

electricalgroundingsafety

I recently bought a new manufactured home. There are instances where people have touched the front door and received an electric shock. Using a non-contact voltage detector, I confirmed that there is detectable voltage present. Using my meter, I see 72V from the frame to ground.

I have an outside meter on a pole, a disconnect box underneath it, and have wiring in sch 80 electrical pvc conduit running under my house feeding up into the breaker box.

enter image description here
enter image description here
enter image description here
Click for larger view

I asked a friend to come and look, and he suggested that I needed a ground wire from the outside disconnect to the inside breaker box. I have a grounding rod connected to the outside disconnect and 3 wires running through the conduit (2 hot, 1 neutral) into the house. There is also a bare copper wire running from the grounding bar in the breaker box that is lugged to the frame under the house.

My first thought was that a screw in the door facing had nicked a wire. After removing every screw, that does not appear to be the cause. Likewise, the problem seem intermittant and isn't experienced on other doors in the house.

Do I need a grounding wire from between the breaker box and the outside disconnect? If so, would I achieve the same thing by running a ground wire from the breaker box to a different grounding rod since it will be ridiculuously hard to try and feed an extra wire back through the conduit now?

Best Answer

Turn off all the breakers, try them one at a time and see when the voltage returns, this should help to locate the problem area. Once you have the area found, turn on all the breakers, except the breaker to that area, and check it again. Now with the problem breaker/breakers off, go through the devices and check if any have a bad wire. I would start with the switches that controls the outside light.