Electrical – RC12L200C Panel box

electricalelectrical-panelwiring

UPDATE: 5 JUL 21:

Almost completed the updates. I cut the wire short on the GFCI attached to the panel, therefore I had to connect the bare ground to the neutral bar. I still need to find a 1/2 inch weather box to replace that old one, then I’ll re-run the wire correctly. I also ran short of UF to completely replace the Romex, so when the rain stops I’ll finish that portion.

UPDATE 27 JUN 21:

I determined today that the yellow Romex lines are going to the addition built on to the Mobile Home. I believe one is for the 4 ceiling fans, 1 is for the bathroom light/GFCI outlet and the other is for the main room outlets (6 in total). Question, can I run UF-B from the main panel to somewhere under the addition and tie the UF and Romex in together within a junction box??????

The panel is a Square D RC12L200c Meter Main

Besides being messy looking, does this look alright?

enter image description here

enter image description here

Best Answer

Alien alert!

That 200A Siemens QN(R) breaker visible in the center of the photo has no business whatsoever being in a Homeline panel such as yours. You'll need to replace it with a HOM2200BB and rearrange the other breakers so that you have four free spaces on the bottom right for it. This also gives you a LK225AN you can mount on the lower right-hand neutral bar so that you can cut the neutral wire (aka the black wire with the yellow stripe) and re-strip it to get a fresh set of strands, then fit it into the new lug.

While we're dealing with breakers, this panel has one too many handle throws in it at the moment; that's trivially dealt with by replacing one of the top pairs (left or right) of HOM120s with a HOM220.

As to other matters...

I noticed that you have several NM cables that appear to be exiting this outdoor panel and heading somewhere that isn't immediately inside. Those cables will fail on you due to the paper wrappers wicking water, so it's best to replace them with either UF cables if they're running free, or with THHN wires if they're in a conduit instead. (There's also what appears to be a UF cable in one of the conduits that should go as well, as that conduit's likely overstuffed as a result.)

Atop that, it appears that whoever installed this used a PVC plumbing pipe for electrical duty, shoving the end of the pipe through the hole instead of using a proper adapter fitting while they were at it. This is no good at all, and needs to be torn out and replaced with a proper conduit run with proper fittings.

Finally, the surge protection device(?) attached to the right side of the panel needs to be examined for proper watertight installation, as I don't know what is going on there, and the conduit entering the box bottom center needs to be fitted with a split conduit bushing of the correct size so that the wires don't abrade against the edge of the conduit.